EFM Data Items: FMS Configuration
The flow measurement configuration data item strings that follow describe FMS Configuration data items supported by CygNet.
Note: The eventItems section of your device template file does not contain configuration data items. However, changes to any data item in the configItem section results in an event being sent to FMS. Configuration data items are omitted from the eventItems section of the device template file to avoid data item duplication within the device template file.
See CygNet Measurement and Using the Configuration Control for more information about configuration data item usage in CygNet Measurement.
FMS Configuration Data Items
Configuration data item strings are listed in the following table along with their corresponding value options.
The table lists configuration data item strings in sections according to type of usage.
|
|
See FMS Data Items Units for information about valid units for configuration data items requiring units.
See Required Device Configuration Data for CygNet Measurement for information about minimum configuration requirements according to calculation/device type.
Gas Analysis Configuration Items
Also valid: Quality configuration items (except those marked liquid-specific)
| FMS Configuration Data Item String | Enum | Data Item Description | Units Required for FMS? | FMS Explorer Description |
|---|---|---|---|---|
| eFMS_CFG_GAS_ANALYSIS_BASE_PRESSURE | 601 | Base pressure | Yes | Base Pressure |
| eFMS_CFG_GAS_ANALYSIS_BASE_TEMPERATURE | 602 | Base temperature | Yes | Base Temperature |
| eFMS_CFG_GAS_ANALYSIS_HEATING_VALUE_BASIS | 603 | Heating Value basis | No | Heating Value Basis |
| eFMS_CFG_HEATING_VALUE_VOLUME_WET | 545 | Heating Value Volume - Wet | Yes | Heating Value Volume (Wet) |
| eFMS_CFG_HEATING_VALUE_VOLUME_DRY | 546 | Heating Value Volume - Dry | Yes | Heating Value Volume (Dry) |
| eFMS_CFG_HEATING_VALUE_VOLUME_AS_DELIVERED | 547 | Heating Value Volume - As delivered | Yes | Heating Value Volume - (As delivered) |
| eFMS_CFG_H2O_PER_VOLUME | 548 | Water - per volume unit | Yes | H2O per volume |
| eFMS_CFG_H2S_PPM | 549 | Hydrogen Sulfide - parts per million | Yes | H2S (PPM) |
| eFMS_CFG_TOTAL_H2S_PPM | 554 | Total Hydrogen Sulfide - parts per million | Yes | Total H2S (PPM) |
| eFMS_CFG_COS_PPM | 550 | Carbonyl Sulfide - parts per million | Yes | COS (PPM) |
| eFMS_CFG_MESH_PPM | 551 | Methanethiol - parts per million | Yes | MESH (PPM) |
| eFMS_CFG_ETSH_PPM | 552 | Ethanethiol - parts per million | Yes | ETSH (PPM) |
| eFMS_CFG_DMS_PPM | 553 | Dimethyl Sulfide - parts per million | Yes | DMS (PPM) |
| eFMS_CFG_SAMPLE_PRESSURE | 555 | Sample pressure | Yes | Sample Pressure |
| eFMS_CFG_SAMPLE_TEMPERATURE | 556 | Sample temperature | Yes | Sample Temperature |
| eFMS_CFG_SAMPLE_COUNT | 557 | Sample count | No | Sample Count |
| eFMS_CFG_SAMPLE_DATE | 512 | Sample date (liquid-specific) | No | Sample Date |
| eFMS_CFG_SAMPLE_RATE | 522 | Sample rate (liquid-specific) | No | Sample Rate |
| eFMS_CFG_SAMPLE_TYPE | 513 | Sample type (liquid-specific) | No | Sample Type Options:
|
| eFMS_CFG_INSTRUMENT_NUMBER | 558 | Instrument number for the sample | No | Instrument Number |
| eFMS_CFG_SAMPLE_TECHNICIAN | 559 | Name of the sample technician | No | Sample Technician |
| eFMS_CFG_SAMPLE_COMMENTS | 560 | Comments for the sample | No | Sample Comments |
| eFMS_CFG_ANALYSIS_TECHNICIAN | 561 | Name of the analysis technician | No | Analysis Technician |
| eFMS_CFG_ANALYSIS_COMMENTS | 562 | Comments for the analysis | No | Analysis Comments |
| eFMS_CFG_HEXANE_PLUS | 563 | Hexane plus | Yes | n-Hexane Plus |
| eFMS_CFG_ETHANE_LC | 564 | Ethane - Liquid Content | Yes | Ethane LC |
| eFMS_CFG_PROPANE_LC | 565 | Propane - Liquid Content | Yes | Propane LC |
| eFMS_CFG_ISOBUTANE_LC | 607 | Isobutane - Liquid Content | Yes | Isobutane LC |
| eFMS_CFG_N_BUTANE_LC | 566 | n-Butane - Liquid Content | Yes | n-Butane LC |
| eFMS_CFG_ISOPENTANE_LC | 567 | Isopentane - Liquid Content | Yes | Isopentane LC |
| eFMS_CFG_N_PENTANE_LC | 568 | n-Pentane - Liquid Content | Yes | n-Pentane LC |
| eFMS_CFG_N_HEXANE_LC | 569 | n-Hexane - Liquid Content | Yes | n-Hexane LC |
| eFMS_CFG_N_HEPTANE_LC | 570 | n-Heptane - Liquid Content | Yes | n-Heptane LC |
| eFMS_CFG_N_OCTANE_LC | 608 | n-Octane - Liquid Content | Yes | n-Octane LC |
| eFMS_CFG_N_NONANE_LC | 609 | n-Nonane - Liquid Content | Yes | n-Nonane LC |
| eFMS_CFG_N_DECANE_LC | 610 | n-Decane - Liquid Content | Yes | n-Decane LC |
| eFMS_CFG_CONDENSATE_LC | 571 | Condensate - Liquid Content | Yes | Condensate LC |
Custom Gas Analysis Configuration Items
Note: To avoid a database misconfiguration, DO NOT re-map the following items once they have been initially mapped.
| FMS Configuration Data Item String | Enum | Data Item Description | Units Required for FMS? | FMS Explorer Description |
|---|---|---|---|---|
| eFMS_CFG_CUSTOM_NUMBER1 | 596 | Custom Number 1 | No | As configured; can be any valid supported numerical configuration item |
| eFMS_CFG_CUSTOM_NUMBER2 | 597 | Custom Number 2 | No | As configured; can be any valid supported numerical configuration item |
| eFMS_CFG_CUSTOM_NUMBER3 | 598 | Custom Number 3 | No | As configured; can be any valid supported numerical configuration item |
| eFMS_CFG_CUSTOM_NUMBER4 | 599 | Custom Number 4 | No | As configured; can be any valid supported numerical configuration item |
| eFMS_CFG_CUSTOM_NUMBER5 | 600 | Custom Number 5 | No | As configured; can be any valid supported numerical configuration item |
Quality Configuration Items
(also valid as Gas Analysis or Metering configuration items, except those marked liquid-specific)
| FMS Configuration Data Item String | Enum | Data Item Description | Units Required for FMS? | FMS Explorer Description |
|---|---|---|---|---|
| eFMS_CFG_METHANE | 30 | Methane (C1) | Yes | Methane |
| eFMS_CFG_ETHANE | 31 | Ethane (C2) | Yes | Ethane |
| eFMS_CFG_PROPANE | 32 | Propane (C3) | Yes | Propane |
| eFMS_CFG_ISOBUTANE | 33 | Isobutane (isoC4) | Yes | Isobutane |
| eFMS_CFG_N_BUTANE | 34 | n-Butane (C4) | Yes | n-Butane |
| eFMS_CFG_ISOPENTANE | 35 | Isopentane (isoC5) | Yes | Isopentane |
| eFMS_CFG_N_PENTANE | 36 | n-Pentane (C5) | Yes | n-Pentane |
| eFMS_CFG_NEO_PENTANE | 37 | Neopentane (neoC5) | Yes | Neopentane |
| eFMS_CFG_N_HEXANE | 38 | n-Hexane (C6) | Yes | n-Hexane |
| eFMS_CFG_N_HEPTANE | 39 | n-Heptane (C7) | Yes | n-Heptane |
| eFMS_CFG_N_OCTANE | 40 | n-Octane (C8) | Yes | n-Octane |
| eFMS_CFG_N_NONANE | 41 | n-Nonane (C9) | Yes | n-Nonane |
| eFMS_CFG_N_DECANE | 42 | n-Decane (C10) | Yes | n-Decane |
| eFMS_CFG_NITROGEN | 43 | Nitrogen (N2) | Yes | Nitrogen |
| eFMS_CFG_CARBON_DIOXIDE | 44 | Carbon dioxide (CO2) | Yes | Carbon Dioxide |
| eFMS_CFG_WATER | 45 | Water (H2O) | Yes | Water |
| eFMS_CFG_HYDROGEN_SULFIDE | 46 | Hydrogen sulfide (H2S) | Yes | Hydrogen Sulfide |
| eFMS_CFG_HYDROGEN | 47 | Hydrogen (H2) | Yes | Hydrogen |
| eFMS_CFG_CARBON_MONOXIDE | 48 | Carbon monoxide (CO) | Yes | Carbon Monoxide |
| eFMS_CFG_OXYGEN | 49 | Oxygen (O2) | Yes | Oxygen |
| eFMS_CFG_HELIUM | 50 | Helium (He) | Yes | Helium |
| eFMS_CFG_ARGON | 51 | Argon (Ar) | Yes | Argon |
| eFMS_CFG_DEW_POINT | 60 | Dew point | No | Dew Point |
| eFMS_CFG_RELATIVE_DENSITY | 58 | Relative density | No | Relative Density |
| eFMS_CFG_VISCOSITY | 61 | Viscosity | Yes | Viscosity |
| eFMS_CFG_HEATING_VALUE_MASS | 56 | Heating value - mass | Yes | (Config) Heating Value Mass |
| eFMS_CFG_HEATING_VALUE_VOLUME | 55 | Heating value - volume | Yes | (Config) Heating Value Volume |
Quality Configuration Items - Gas-Specific
| FMS Configuration Data Item String | Enum | Data Item Description | Units Required for FMS? | FMS Explorer Description |
|---|---|---|---|---|
| eFMS_CFG_COMPRESSIBILITY | 59 | Compressibility (gas-specific) | No | Compressibility |
| eFMS_CFG_HEATING_VALUE_BASIS | 57 | Heating value basis (gas-specific) | No | (Config) Heating Value Basis Options:
|
Quality Configuration Items - Liquid-Specific
(not currently supported in all FMS Explorer controls)
| FMS Configuration Data Item String | Enum | Data Item Description | Units Required for FMS? | FMS Explorer Description |
|---|---|---|---|---|
| eFMS_CFG_ETHYLENE | 540 | Ethylene (liquid-specific) | Yes | Ethylene |
| eFMS_CFG_PROPYLENE | 541 | Propylene (liquid-specific) | Yes | Propylene |
Metering Configuration Items
Also valid: Quality configuration items (except those marked liquid-specific)
| FMS Configuration Data Item String | Enum | Data Item Description | Units Required for FMS? | FMS Explorer Description |
|---|---|---|---|---|
| eFMS_CFG_ATMOSPHERIC_PRESSURE | 24 | Atmospheric pressure | Yes | Atmospheric Pressure |
| eFMS_CFG_BASE_PRESSURE | 10 | Base pressure | Yes | (Config) Base Pressure |
| eFMS_CFG_BASE_TEMPERATURE | 11 | Base temperature | Yes | (Config) Base Temperature |
| eFMS_CFG_CALIBRATION_FACTOR | 78 | Calibration factor | No | Calibration Factor |
| eFMS_CFG_CONE_DIAMETER | 18 | Cone diameter | Yes | Cone Diameter |
| eFMS_CFG_CONE_MATERIAL | 20 | Cone material | No | Cone Material Options:
Note: This field is "Unspecified" for devices that do not return a material type value. In these cases, a (non-zero) thermal expansion coefficient value (eFMS_CFG_CONE_COEFFICIENT_THERMAL_EXPANSION) is required for calculation to succeed. |
| eFMS_CFG_CONE_REF_TEMP | 19 | Cone reference temperature | Yes | Cone Ref Temp |
| eFMS_CFG_CONTRACT_HOUR | 9 | Contract hour | No | Contract Hour |
| eFMS_CFG_DISCHARGE_COEFFICIENT | 27 | Discharge coefficient | No | Discharge Coefficient |
| eFMS_CFG_DP_ALARM_HIGH | 107 | DP alarm - high | Yes | DP Alarm High |
| eFMS_CFG_DP_ALARM_LOW | 106 | DP alarm - low | Yes | DP Alarm Low |
| eFMS_CFG_DP_BACKFLOW_ALARM | 114 | DP alarm - backflow | Yes | DP Backflow Alarm |
| eFMS_CFG_DP_CALIBRATE_HIGH | 116 | DP calibrate - high | Yes | DP Calibrate High |
| eFMS_CFG_DP_CALIBRATE_LOW | 115 | DP calibrate - low | Yes | DP Calibrate Low |
| eFMS_CFG_DP_TAPS_TYPE | 21 | DP taps type | No | DP Tap Style Options:
|
| eFMS_CFG_DP_TRANSDUCER_RANGE_HIGH | 101 | DP transducer range - high | Yes | DP Transducer Range High |
| eFMS_CFG_DP_TRANSDUCER_RANGE_LOW | 100 | DP transducer range - low | Yes | DP Transducer Range Low |
| eFMS_CFG_ELEVATION | 86 | Elevation | Yes | Elevation |
| eFMS_CFG_FIXED_TEMP | 85 | Fixed temperature | Yes | Fixed Temp (if eFMS_CFG_USE_LIVE_TEMP = No) |
|
eFMS_CFG_FLASH_GAS_FACTOR |
611 |
Flash gas factor (liquid-specific) |
No |
Flash Gas Factor |
| eFMS_CFG_FLOW_COMPUTER_ID | 133 |
Flow computer ID |
No | Flow Computer ID |
| eFMS_CFG_FLOW_COMPUTER_BRAND | 134 |
Flow computer brand |
No | Flow Computer Brand |
| eFMS_CFG_FLOW_COMPUTER_MODEL | 135 |
Flow computer model |
No | Flow Computer Model |
| eFMS_CFG_FLOW_COMPUTER_SOFTWARE_VERSION | 136 |
Flow computer software version |
No | Flow Computer Software Version |
| eFMS_CFG_FLOW_RATE_ALARM_HIGH | 113 | Flow rate - high | Yes | Flow Rate Alarm High |
| eFMS_CFG_FLOW_RATE_ALARM_LOW | 112 | Flow rate - low | Yes | Flow Rate Alarm Low |
| eFMS_CFG_FLUID_TYPE | 81 | Fluid type | No | Fluid Type Options:
|
| eFMS_CFG_ISENTROPIC_EXPONENT | 82 | Isentropic exponent | No | Isentropic Exponent |
| eFMS_CFG_LOW_FLOW_CUTOFF_DP | 89 | Low flow cutoff - differential pressure | Yes | Low Flow Cutoff DP (can apply to Orifice or Cone device type) |
| eFMS_CFG_LOW_FLOW_CUTOFF_FLOW_RATE | 90 | Low flow cutoff - volume flow rate | Yes | Low Flow Cutoff Flow Rate (can apply to Orifice, Turbine, Ultrasonic, Cone, or Coriolis device type) |
| eFMS_CFG_LOW_FLOW_CUTOFF_MASS | 128 | Low flow cutoff - mass flow rate | Yes | Low Flow Cutoff Mass (can apply to Coriolis device type) |
| eFMS_CFG_LOW_FLOW_CUTOFF_PULSE_INTERVAL | 91 | Low flow cutoff - pulse interval | Yes | Low Flow Cutoff Pulse Interval (can apply to Turbine, Ultrasonic, or Coriolis device type) |
| eFMS_CFG_METER_DESC | 8 | Meter description | No | Device Description |
| eFMS_CFG_METER_FACTOR | 25 | Meter factor | No | Meter Factor |
| eFMS_CFG_METER_ID | 7 | Meter ID | No | Device Name |
| eFMS_CFG_METER_TUBE_INSIDE_DIAMETER | 12 | Meter tube inside diameter | Yes | Meter Tube Inside Diameter |
| eFMS_CFG_METER_TUBE_MATERIAL | 14 | Meter tube material | No | Meter Tube Material Options:
Note: This field is "Unspecified" for devices that do not return a material type value. In these cases, a (non-zero) thermal expansion coefficient value (eFMS_CFG_PIPE_COEFFICIENT_THERMAL_EXPANSION) is required for calculation to succeed. |
| eFMS_CFG_METER_TUBE_REF_TEMP | 13 | Meter tube reference temperature | Yes | Meter Tube Ref Temp |
| 1 | Meter type | No | Device Type Options:
|
|
| eFMS_CFG_ORIFICE_PLATE_BORE_SIZE | 15 | Orifice plate bore size | Yes | Orifice Plate Bore Size |
| eFMS_CFG_ORIFICE_PLATE_MATERIAL | 17 | Orifice plate material | No | Orifice Plate Material Options:
Note: This field is "Unspecified" for devices that do not return a material type value. In these cases, a (non-zero) thermal expansion coefficient value (eFMS_CFG_PIPE_COEFFICIENT_THERMAL_EXPANSION) is required for calculation to succeed. |
| eFMS_CFG_ORIFICE_PLATE_REF_TEMP | 16 | Orifice plate reference temperature | Yes | Orifice Plate Ref Temp |
| eFMS_CFG_SP_ALARM_HIGH | 109 | SP alarm - high | Yes | SP Alarm High |
| eFMS_CFG_SP_ALARM_LOW | 108 | SP alarm - low | Yes | SP Alarm Low |
| eFMS_CFG_SP_CALIBRATE_HIGH | 118 | SP calibrate - high | Yes | SP Calibrate High |
| eFMS_CFG_SP_CALIBRATE_LOW | 117 | SP calibrate - low | Yes | SP Calibrate Low |
| eFMS_CFG_SP_SENSOR_TYPE | 23 | SP sensor type | No | SP Sensor Type Options:
|
| eFMS_CFG_SP_TAP_LOCATION | 22 | SP tap location | No | SP Tap Location Options:
|
| eFMS_CFG_SP_TRANSDUCER_RANGE_LOW | 102 | SP transducer range - low | Yes | SP Transducer Range Low |
| eFMS_CFG_SP_TRANSDUCER_RANGE_HIGH | 103 | SP transducer range - high | Yes | SP Transducer Range High |
| eFMS_CFG_TEMP_ALARM_HIGH | 111 | Temp alarm - high | Yes | Temp Alarm High |
| eFMS_CFG_TEMP_ALARM_LOW | 110 | Temp alarm - low | Yes | Temp Alarm Low |
| eFMS_CFG_TEMP_CALIBRATE_HIGH | 120 | Temp calibrate - high | Yes | Temp Calibrate High |
| eFMS_CFG_TEMP_CALIBRATE_LOW | 119 | Temp calibrate - low | Yes | Temp Calibrate Low |
| eFMS_CFG_TEMP_CALIBRATE_ZERO | 121 | Temp calibrate - zero | Yes | Temp Calibrate Zero |
| eFMS_CFG_TEMP_TRANSDUCER_RANGE_LOW | 104 | Temp transducer range - low | Yes | Temp Transducer Range Low |
| eFMS_CFG_TEMP_TRANSDUCER_RANGE_HIGH | 105 | Temp transducer range - high | Yes | Temp Transducer Range High |
| eFMS_CFG_USE_LIVE_TEMP | 84 | Use live temperature | No | Use Live Temp Options:
|
| eFMS_CFG_USE_LIVE_K_FACTOR | 125 | Use live K factor | No | Use Live K Factor Options:
|
| eFMS_CFG_USE_LIVE_METER_FACTOR | 126 | Use live meter factor | No | Use Live Meter Factor Options:
|
Metering Configuration Items - Gas-Specific
| FMS Configuration Data Item String | Enum | Data Item Description | Units Required for FMS? | FMS Explorer Description |
|---|---|---|---|---|
| eFMS_CFG_AGA3_EXPANDED_RANGE | 88 | AGA 3 Expanded Range (gas-specific) | No | AGA 3 Expanded Range Options:
|
| eFMS_CFG_AGA8_EXPANDED_RANGE See AGA 8 Data Ranges for more information. |
87 | AGA 8 Expanded Range (gas-specific) | No | AGA 8 Expanded Range Options:
|
| eFMS_CFG_BASE_COMPRESSIBILITY_OF_AIR | 83 | Standard air compressibility (gas-specific) | No | Base Compressibility of Air |
| eFMS_CFG_CALC_METHOD_DISCHARGE_COEFFICIENT | 5 | Discharge coefficient calc method (gas-specific) | No | Discharge Coefficient Calc Options:
|
| eFMS_CFG_CALC_METHOD_FPV | 3 | Compressibility calc method (gas-specific) | No | FPV Calc Options:
|
| eFMS_CFG_CALC_METHOD_GAS_EXPANSION_FACTOR | 6 | Gas expansion factor calc method (gas-specific) | No | Gas Expansion Factor Calc Options:
|
| eFMS_CFG_CALC_METHOD_HV | 4 | Heating value calc method (gas-specific) | No | HV Calc Options:
Note: For gas analysis, FMS calculations are based on GPA 2172-09. See CygNet Measurement Data Calculation for more information. |
| eFMS_CFG_CALC_METHOD_PRIMARY | 2 | Primary calc method (gas-specific) | No | Primary Calc Options:
|
| eFMS_CFG_INTEGRAL_VALUE_VARIABLES | 28 | Variables included in IV (gas-specific) | No | IV Definition Options:
|
| eFMS_CFG_GAS_K_FACTOR_MASS | 127 | K factor - mass (gas-specific) | Yes | K Factor Mass |
| eFMS_CFG_GAS_K_FACTOR_VOLUME | 26 | K factor - volume (gas-specific) | Yes | K Factor Volume |
| eFMS_CFG_CONE_COEFFICIENT_THERMAL_EXPANSION | 130 | Cone thermal expansion coefficient (gas-specific) | Yes | Cone Expansion Coefficient |
| eFMS_CFG_ORIFICE_COEFFICIENT_THERMAL_EXPANSION | 75 | Orifice (linear) thermal expansion coefficient (gas-specific) | Yes | Orifice Expansion Coefficient |
| eFMS_CFG_PIPE_COEFFICIENT_THERMAL_EXPANSION | 76 | Pipe (linear) thermal expansion coefficient (gas-specific) | Yes | Pipe Expansion Coefficient |
| eFMS_CFG_LINEAR_CURVE_TYPE | 129 | Linear curve type (gas-specific) | No | Linear Curve Type Options:
|
| eFMS_CFG_USE_CORIOLIS_PRESSURE_EFFECT | 122 | Use coriolis pressure effect (gas-specific) | No | Use Coriolis Pressure Effect Options:
|
| eFMS_CFG_CORIOLIS_PRESSURE_EFFECT | 123 | Percent of rate per gauge pressure (gas-specific) | Yes | Coriolis Pressure Effect |
| eFMS_CFG_CORIOLIS_CALIBRATION_PRESSURE | 124 | Pressure at which the pressure effect was calibrated (gas-specific) | Yes | Coriolis Calibration Pressure |
| eFMS_CFG_WATER_VAPOR_CORRECTION_FACTOR | 74 | Water vapor correction factor (gas-specific) | No | Water Vapor Correction factor |
| eFMS_CFG_WELL_STREAM_FACTOR | 77 | Well stream factor (gas-specific) | No | Well Stream factor |
Metering Configuration Items - Liquid-Specific
(not currently fully supported in all FMS Explorer controls)
| FMS Configuration Data Item String | Enum | Data Item Description | Units Required for FMS? | FMS Explorer Description |
|---|---|---|---|---|
| eFMS_CFG_DENSITY_METER_FACTOR | 537 | Density meter factor (liquid-specific) | No | DMF |
| eFMS_CFG_MASS_FLOW_RATE_ALARM_HIGH | 132 | Mass flow rate alarm - high (liquid-specific) | Yes | Flow Rate Alarm High |
| eFMS_CFG_MASS_FLOW_RATE_ALARM_LOW | 131 | Mass flow rate alarm - low (liquid-specific) | Yes | Flow Rate Alarm Low |
| eFMS_CFG_LIQ_K_FACTOR_MASS | 543 | K factor - mass (liquid-specific) | Yes | K Factor Mass |
| eFMS_CFG_LIQ_K_FACTOR_VOLUME | 542 | K factor - volume (liquid-specific) | Yes | K Factor Volume |
| eFMS_CFG_LIQUID_CALC_METHOD | 539 | Liquid calculation method (liquid-specific) | No | Liquid Calculation Method Options:
|
| eFMS_CFG_LIQUID_PRODUCT_INDEX | 544 | Product index (liquid-specific) | No | Product Index |
| eFMS_CFG_TOTALIZER_DIGITS | 538 | Totalizer digits (liquid-specific) | No | Totalizer Digits |
| eFMS_CFG_SHRINK_FACTOR | 604 | Shrink factor (liquid-specific) | No | Shrink Factor |
| eFMS_CFG_STOCK_TANK_DENSITY | 605 | Stock tank - density (liquid-specific) | Yes | Stock Tank Density |
| eFMS_CFG_STOCK_TANK_SW | 606 | Stock tank - sediment and water (liquid-specific) | Yes | Stock Tank S&W |
|
|
|
|
|
|
Custom Configuration Items - Gas-Specific
Note: To avoid a database misconfiguration, DO NOT re-map the following items once they have been initially mapped.
| FMS Configuration Data Item String | Enum | Data Item Description | Units Required for FMS? | FMS Explorer Description |
|---|---|---|---|---|
| eFMS_CFG_CUSTOM1 | 500 | Custom 1 | No | As configured; can be any valid configuration item |
| eFMS_CFG_CUSTOM2 | 501 | Custom 2 | No | As configured; can be any valid configuration item |
| eFMS_CFG_CUSTOM3 | 502 | Custom 3 | No | As configured; can be any valid configuration item |
| eFMS_CFG_CUSTOM4 | 503 | Custom 4 | No | As configured; can be any valid configuration item |
| eFMS_CFG_CUSTOM5 | 504 | Custom 5 | No | As configured; can be any valid configuration item |
| eFMS_CFG_CUSTOM6 | 505 | Custom 6 | No | As configured; can be any valid configuration item |
| eFMS_CFG_CUSTOM7 | 506 | Custom 7 | No | As configured; can be any valid configuration item |
| eFMS_CFG_CUSTOM8 | 507 | Custom 8 | No | As configured; can be any valid configuration item |
| eFMS_CFG_CUSTOM9 | 508 | Custom 9 | No | As configured; can be any valid configuration item |
| eFMS_CFG_CUSTOM10 | 509 | Custom 10 | No | As configured; can be any valid configuration item |
Custom Configuration Items - Gas-Specific
Note: To avoid a database misconfiguration, DO NOT re-map the following items once they have been initially mapped.
See Configuring Custom Device Data in the CygNet Measurement section for more information.
| FMS Configuration Data Item String | Enum | Data Item Description | Units Required for FMS? | FMS Explorer Description |
|---|---|---|---|---|
| eFMS_CFG_ACCUMULATED_VOLUME | 517 | Accumulated volume (gas-specific) | Yes | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_AIR | 536 | Air (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_COLD_START_DATETIME | 515 | Cold start date/time (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_CONTRACT_DAY | 523 | Contract day (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_DELIVERY_DATE | 519 | Delivery date (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_DP_CALIBRATE_MID | 525 | DP calibrate - mid (gas-specific) | Yes | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_EXPANSION_FACTOR | 530 | Expansion factor (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_FLOWING_TEMPERATURE_FACTOR | 533 | Flowing temperature factor (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_LATITUDE | 510 | Latitude (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_LONGITUDE | 511 | Longitude (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_METER_ACCESS_DATETIME | 514 | Meter access date/time (liquid-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_METER_SERIAL_NUMBER | 518 | Meter serial number (liquid-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_ORIFICE_FITTING_TYPE | 521 | Orifice fitting type (liquid-specific) | No | Can be mapped as a custom gas configuration item. Options:
|
| eFMS_CFG_ORIFICE_FLOW_FACTOR | 528 | Orifice flow factor (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_POWER_SOURCE | 520 | Power source (gas-specific) | No | Can be mapped as a custom gas configuration item. Options:
|
| eFMS_CFG_PRESSURE_BASE_FACTOR | 531 | Pressure base factor (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_RELATIVE_DENSITY_FACTOR | 534 | Relative density factor (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_REYNOLDS_FACTOR | 529 | Reynolds factor (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_SP_CALIBRATE_MID | 526 | SP calibrate - mid (gas-specific) | Yes | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_SUPERCOMPRESSIBILITY_FACTOR | 535 | Supercompressibility factor (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_TEMP_CALIBRATE_MID | 527 | Temp calibrate - mid (gas-specific) | Yes | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_TEMPERATURE_BASE_FACTOR | 532 | Temperature base factor (gas-specific) | No | Can be mapped as a custom gas configuration item. |
| eFMS_CFG_WARM_START_DATETIME | 516 | Warm start date/time (gas-specific) | No | Can be mapped as a custom gas configuration item. |
More: